If the two circuits feed two different services, I don't think so.Can I run the Enphase circuits for 2 ADU's in the same conduit?
(Both PV arrays go on the roof of main house because it has the 4-meter bank for all 4 units. 2 detached ADUs are in the back. Each PV system goes to a separate Combiner Box and service.)
I am aware of no such prohibition in the NEC. Reference?If the two circuits feed two different services, I don't think so.
No reference; just a guess.I am aware of no such prohibition in the NEC. Reference?
Cheers, Wayne
Incorrect guess AFAIK.No reference; just a guess.
They don't actually do their own code they just have an unusually large number of significant ammendments that are vestiges from when they did actually did their own code decades ago.San Francisco has an interesting local electrical code. Not that many cities do their own code but something to be aware of.
Yes, it's a modified CA electrical code, which is a modified NEC, but it's still their electrical code that they made. Not following it can cause a lot of problems. The county of Los Angeles has their own electrical code that is a modified CA electrical code. Got to keep an eye out for these.They don't actually do their own code they just have an unusually large number of significant ammendments that are vestiges from when they did actually did their own code decades ago.
An inane restriction. Did they also regulate the number of service disconnects beyond what the NEC allows? If not, just throw a little night light on your supply side interconnection and call it a second service disconnect with a load-side interconnection.the municipal electric utility banned supply side PV interconnections
I know of a couple of jurisdictions relatively nearby where supply side PV interconnections are not allowed, and one where supply side interconnections are the only ones permitted. There is even one where any PV interconnections must be made outside the customer's meter with its own meter. The last company I worked for maintained an on line spreadsheet that documented the unique rules and regulations regarding PV systems for every jurisdiction we operated in. The last time I saw it it was four or five sheets long.An inane restriction.
If the 2 systems have separate Envoys, I would keep physical separation of the wiring from each and not put in the same conduit to prevent powerline communication crosstalk.Can I run the Enphase circuits for 2 ADU's in the same conduit?
(Both PV arrays go on the roof of main house because it has the 4-meter bank for all 4 units. 2 detached ADUs are in the back. Each PV system goes to a separate Combiner Box and service.)
I've found that things can get weird with municipal utilities. There can be little or no separation between the utility and the city building department so the utility engineers can dictate some of the local building code requirements.An inane restriction. Did they also regulate the number of service disconnects beyond what the NEC allows? If not, just throw a little night light on your supply side interconnection and call it a second service disconnect with a load-side interconnection.