I am adding (2) mini-splits to my home, 240v, 15a max OCP per unit.
I have room for one DP breaker in my QO panel, I am not interested in adding a sub panel at this time.
I would like to run 10-2 UF, off one 30A DP GFCI(per Mitsubishi) breaker, this circuit would then hit (2) 30a, fusible A/C disconnects, each with 12A time-delay fuses installed.
While an unusual installation, does anyone see an issue with it?
The wire is protected by the breaker, the mini-splits are protected by the fuses.
Thanks for the feedback...
I have room for one DP breaker in my QO panel, I am not interested in adding a sub panel at this time.
I would like to run 10-2 UF, off one 30A DP GFCI(per Mitsubishi) breaker, this circuit would then hit (2) 30a, fusible A/C disconnects, each with 12A time-delay fuses installed.
While an unusual installation, does anyone see an issue with it?
The wire is protected by the breaker, the mini-splits are protected by the fuses.
Thanks for the feedback...