On a current remodeling project our client wants to put all motors on VFDs. We discovered two ? 5 Hp, 17.5 amp, 208 volt, 3 phase motors on one 50 amp breaker. Our VFD manufacturer indicates that a 5 Hp VFD has an input of 16.7 amps and requires a 30 amp breaker. The panelboard with the 50 amp breaker is full. No spare space. The wire appears to be #8 TW rated at 40 amps and can easily be replaced if need be. My question is, is the 50 amp breaker adequate or should it be increased to a 60 and replace the wire with #6 THHN, 75 degree C rated at 65 amps. If the 50 amp breaker is adequate, is the existing #8 TW wire adequate.?
Also, as a side question, the motor is rated at 17.5 amps and the input to the drive is 16.7 amps. How do you ever get the full horsepower out of the motor?
Also, as a side question, the motor is rated at 17.5 amps and the input to the drive is 16.7 amps. How do you ever get the full horsepower out of the motor?