Update on phase converter and buck-boost transformer.
Update on phase converter and buck-boost transformer.
Thanks for your responses. Sorry for the delay. We,ve been a little pre-occupied, what with Mount Redoubt puffing ashes all over the Kenai peninsula.
The Heidelburg press: Previous installation was served by 120-240 4 Wire. The 3 phase motor is made by Siemens. I have communicated with them and they say: "This motor cannot be run at 209, you must use 230V". It does include a control system which needs 2-wire, 120 volt.
The shop: Is located in a complex of eight small businesses. The initial installation was supposed to be 120-240, 4 wire, delta. But it turned out differently. All businesses have single phase, 120-208. I've interviewed some of them and they don't realize that they have 208, not 240. No body every cared until my customer came along, with a three phase press. To properly supply this customer, the power company would have to put in a 3 phase meter, and run another wire the length of the building. Not going to happen.
ARCO has supplied drawings that show how to install the Roto-Phase with a Buck/Boost transformer.
I'm uncomfortable with the neutral situation and the single phase control feed.
The customer already has the Roto-Phase. By the time he pays for a buck/boost, a mag. starter, disconnect switch, cabinet, and wiring he is going to be in for a lot more bucks than he figured on.
Thanks again. All advice gladly accepted.
Maynard.