Just wanted to say thanks to the organizers of this forum for help resolving service voltage issue at a new retail store we just designed (attached link for original issue and threads). Quick summary: Our service from the POCO was a true 2-phase, 5-wire antiquated system. We wanted to re-use the service instead of having to heavy up the service which would have caused us to install a transformer vault within the store ($$$$). Luckily through this forum, I discovered the magical Scott T transformer (we affectionately call him Scotty now). We specified a custom built 200KVA Scott T transformer by Hammond Power which converted the incoming 2-phase, 5-wire service to a 208V, 3-phase, 4-wire service. The store opened on time and on budget thanks to Scotty. Attached photo of nameplate. Photos of the existing condition located on original thread.