Good morning everyone. Im stumped on this question and would love to have some help to clearify it
Q: determin the Maximum current setting permitted for overload protection for a motor that has a thermal protector integral with the motor, given the following: 7.5 hp wound rotor type, two -phase 4-wire ac, 230 volts
A. 19 amps
B. 26.6 amps
C. 29.6 amps
D. 32.3 amps
i have the answer, its C. 29.6 amps but can't figure out how to get that answer:-?
all i can find is art: 430.149 table in nec 2002?? anyone. i though it would be x1.15 or even 1.25 but nothing. thanks
Q: determin the Maximum current setting permitted for overload protection for a motor that has a thermal protector integral with the motor, given the following: 7.5 hp wound rotor type, two -phase 4-wire ac, 230 volts
A. 19 amps
B. 26.6 amps
C. 29.6 amps
D. 32.3 amps
i have the answer, its C. 29.6 amps but can't figure out how to get that answer:-?
all i can find is art: 430.149 table in nec 2002?? anyone. i though it would be x1.15 or even 1.25 but nothing. thanks