I am working on a project that has 2 phase... Nothing else is available... Commercial building ...4 stories, elevator, fire pump, resteraunt. Upper floor being convert to apts.
Existing 75 kva 2 phase 120/240 to 3 phase 120/240 for restaurant ...
2 phase to 3 phase for fire pumps 120/240
2 phase 120/240 to 3 phase 120/208 for elevator...
4 taps 100 amp (2 phase) with meters and disconnects for 3 floors and house panel , tap for fire,pumps
Then CT cabinet , 200 amp disconnect for 75 kva transformer to the Resturant ...
I need to add at least 6 meters and disconnects..
I do not like the way the engineer has this spec,d ..there is no room , all the fire pump piping in the way,
There is apox 400/600 amp service 4/0 copper 2 phase ...spec to be upgraded to 1000 amp with new disconnect ...(2 phase



Existing 75 kva 2 phase 120/240 to 3 phase 120/240 for restaurant ...
2 phase to 3 phase for fire pumps 120/240
2 phase 120/240 to 3 phase 120/208 for elevator...
4 taps 100 amp (2 phase) with meters and disconnects for 3 floors and house panel , tap for fire,pumps
Then CT cabinet , 200 amp disconnect for 75 kva transformer to the Resturant ...
I need to add at least 6 meters and disconnects..
I do not like the way the engineer has this spec,d ..there is no room , all the fire pump piping in the way,
There is apox 400/600 amp service 4/0 copper 2 phase ...spec to be upgraded to 1000 amp with new disconnect ...(2 phase