Performed some kitchen remodeling with new fixtures & added outlets to exisiting kitchen 20 amp circuit with a shared neutral. Originally had split receptacles, i.e. one circuit on lower half of duplex, second circuit on upper half. I maintained that configuration.
Now I want to add GFCI protection so I went to the forum and looked at the archives - very confusing and far from a unanimity of opinion on this subject! It did seem that if I wanted to do this, esp. given the split receptacle configuration, my only option was a 2 pole 20 amp GFCI Breaker which I purchased and installed.
It didn't work. As soon as power feeds the breaker it trips. This particular breaker (Siemens)has terminals for each of the power loads and the load neutral. There is also a heavy gauge white lead which is terminated at the neutral bus.
Next I started trouble shooting. Since this installation works fine with a regular 20 amp breaker (single pole on each load phase) I didn't think the problem was in the load side wiring. I checked my connections at the panel - the breaker keeps tripping. Next I re-instlalled the single pole breakers and took a reading on the gounded conductor looking for current which might have tripped the GFCI. Less than a .1 amp so I assume this confirms my instinct that the wiring isn't faulty or I have an existing ground fault in the circuits.
As I see it there are three options: 1. The breaker is defective or 2. I cannot put GFCI protection on this type of circuit (how can that be - I thought that is what this breaker configuration was all about) or 3. I've got some sort of wiring problem to the outlets and luminaries on this circuit which isn't causing a problem with regular breakers but is tripping the GFCI. I need you input. Hopefully the wise heads on this forum can point me in the right direction.
Thanks.
Now I want to add GFCI protection so I went to the forum and looked at the archives - very confusing and far from a unanimity of opinion on this subject! It did seem that if I wanted to do this, esp. given the split receptacle configuration, my only option was a 2 pole 20 amp GFCI Breaker which I purchased and installed.
It didn't work. As soon as power feeds the breaker it trips. This particular breaker (Siemens)has terminals for each of the power loads and the load neutral. There is also a heavy gauge white lead which is terminated at the neutral bus.
Next I started trouble shooting. Since this installation works fine with a regular 20 amp breaker (single pole on each load phase) I didn't think the problem was in the load side wiring. I checked my connections at the panel - the breaker keeps tripping. Next I re-instlalled the single pole breakers and took a reading on the gounded conductor looking for current which might have tripped the GFCI. Less than a .1 amp so I assume this confirms my instinct that the wiring isn't faulty or I have an existing ground fault in the circuits.
As I see it there are three options: 1. The breaker is defective or 2. I cannot put GFCI protection on this type of circuit (how can that be - I thought that is what this breaker configuration was all about) or 3. I've got some sort of wiring problem to the outlets and luminaries on this circuit which isn't causing a problem with regular breakers but is tripping the GFCI. I need you input. Hopefully the wise heads on this forum can point me in the right direction.
Thanks.