will breaker trip instataneously,if neutral is bonded to ground at service equipment with three wire configuration at dryer outlet?
Why should it unless some fault current is flowing?will breaker trip instataneously,if neutral is bonded to ground at service equipment with three wire configuration at dryer outlet?
Why should it unless some fault current is flowing?
Now if you are talking about a 240V GFCI breaker, that would be a different question.
As long as the neutral (grounded) conductor remains intact, there will be no immediate difference between bonding the dryer ground to the neutral and keeping it isolated by using a fourth wire. There will be neutral current in the ground system if there is some other connection between the dryer and grounded metal, such as a gas pipe. But that will not blow a simple breaker on current.