2 pole breaker

Status
Not open for further replies.

pipedope

Member
May 2 circuits, such as a lighting circuit and another receptacle circuit, be tied to a 2pole breaker so they will both be interupted at the same time? One leg on each pole of the circuit breaker. Do circuits have to have individual single pole breakers or would this method be approved? Also is it approved to use individual single pole breakers as a double pole if the handles are mechanically connected by a tie?
 
Re: 2 pole breaker

No you can not use (2) 1p breakers with a handle tie as a substitute for a 2p breaker where a 2p breaker is required.
We (2) 1p breakers are tied together with a handle tie if there is an overload or short circuit on one pole the other will not trip. In other words the handle of one pole moving to the tripped position will not pull the other handle along with it. A 2p breaker that "appears" to be simply (2) 1p breakers simply tied together with a handle tie isn't. The key word is "common trip."
The trip mechanisms are tied together internally such that if one breaker calls for a trip it will activate the other pole to trip also. Thus the term "common trip."
 
Re: 2 pole breaker

May 2 circuits, such as a lighting circuit and another receptacle circuit, be tied to a 2pole breaker so they will both be interupted at the same time?

Yes


Do circuits have to have individual single pole breakers or would this method be approved?

No they don't have to. This method is okay.


Also is it approved to use individual single pole breakers as a double pole if the handles are mechanically connected by a tie?

I'm going to answer differently than templdl and say that this is also okay as long as the tie pulls the other breaker into the off position.
 
Re: 2 pole breaker

Paul,
I'm going to answer differently than templdl and say that this is also okay as long as the tie pulls the other breaker into the off position.
If they are (2) individual breakers ties together with a handle tie if one breaker calls for a trip that breaker(trips automatically), NO that handle tie it WILL NOT TRIP or PULL the handle of the other breaker to the OFF or tripped position. You may get lucky to get a manufacturer's breaker who will but none that I know of.
Dave
 
Re: 2 pole breaker

Handle ties are permitted when the only requirement is for simultaneous manual operation. For automatic operation, the internal-trip mechanism is required.
 
Re: 2 pole breaker

This was posted twice, and the other one has more replies. So I am closing this thread. Please continue the discussion here.
 