Will a 2 pole gfci circuit breaker work properly if it is connected to (2) 120V loads sharing a common neutral conductor? I am unable to find a wiring diagram online for a HOM220GFCI Breaker. I could see having problems trying to accomplish this with 2 SP GFCI breakers.Thanks.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Will a 2 pole gfci circuit breaker work properly if it is connected to (2) 120V loads sharing a common neutral conductor? I am unable to find a wiring diagram online for a HOM220GFCI Breaker. I could see having problems trying to accomplish this with 2 SP GFCI breakers.Thanks.

If the two pole breaker has a neutral lead pigtail, then it should work.
 