Z zaid Member Jun 18, 2003 #1 I know that 2 pole GFCI Circuit Breaker is designed for multiwire brach circuit (that is 3 wire circuit 2 phase and common neutral.) can we install 2p gfci circuit breaker to protect 220V receptacle (two wire circuit)??
I know that 2 pole GFCI Circuit Breaker is designed for multiwire brach circuit (that is 3 wire circuit 2 phase and common neutral.) can we install 2p gfci circuit breaker to protect 220V receptacle (two wire circuit)??
B bennie Esteemed Member Jun 21, 2003 #2 Re: 2 pole GFCI Circuit Breaker Yes, you can. Connect the neutral (white) wire to the panel bus. The trip circuit operates on 120 volts. [ June 21, 2003, 07:38 PM: Message edited by: bennie ]
Re: 2 pole GFCI Circuit Breaker Yes, you can. Connect the neutral (white) wire to the panel bus. The trip circuit operates on 120 volts. [ June 21, 2003, 07:38 PM: Message edited by: bennie ]