2 pole GFCI Circuit Breaker

Status
Not open for further replies.

zaid

Member
I know that 2 pole GFCI Circuit Breaker is designed for multiwire brach circuit (that is 3 wire circuit 2 phase and common neutral.) can we install 2p gfci circuit breaker to protect 220V receptacle (two wire circuit)??
 

bennie

Esteemed Member
Re: 2 pole GFCI Circuit Breaker

Yes, you can. Connect the neutral (white) wire to the panel bus.

The trip circuit operates on 120 volts.

[ June 21, 2003, 07:38 PM: Message edited by: bennie ]
 
Status
Not open for further replies.
Top