Hi
Do you thing that any 240v, 2-pole loads such as motors, electr. car chargers, 240v heat lamps would operate better , briter,.....@ 240v, Delta config. - phase-A (120v) and phase-B (208v)
than if they were connected to 240V (two 120V phases) ??????

Is it okay to connect 240V heat lamp to Delta system using high leg, 208v and 120v leg ????

Tanx
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Hi
Do you thing that any 240v, 2-pole loads such as motors, electr. car chargers, 240v heat lamps would operate better , briter,.....@ 240v, Delta config. - phase-A (120v) and phase-B (208v)
than if they were connected to 240V (two 120V phases) ??????

No, they have the same voltage either way.
Is it okay to connect 240V heat lamp to Delta system using high leg, 208v and 120v leg ????

Tanx

Yes, you can connect your 240V single phase loads A-B, B-C or A-C.
 