A 5 hp 230v 1 phase blower motor is marked 3450 rpm. It was found to have only a 30 amp breaker at the panel supplying it, and it has been tripping at startup. 30 amp breaker seems small.
My question is: table 430.248 says ampacity and short circuit ground fault protection is supposed to be based on a 28 amp full load current. But the table says it is for “normal” speed motors. Most induction motors I’m familiar with are 4 pole 1745 or so RPM. I’m not aware of the nec defining what “normal” speeds are. Is a 2 pole motor that spins at 3450 rpms considered a “normal” speed motor, where I can use the table 430.248, or not? Sure would be nice if they would define normal speed.
My question is: table 430.248 says ampacity and short circuit ground fault protection is supposed to be based on a 28 amp full load current. But the table says it is for “normal” speed motors. Most induction motors I’m familiar with are 4 pole 1745 or so RPM. I’m not aware of the nec defining what “normal” speeds are. Is a 2 pole motor that spins at 3450 rpms considered a “normal” speed motor, where I can use the table 430.248, or not? Sure would be nice if they would define normal speed.