2-Pole vs 3-Pole Breaker

Status
Not open for further replies.

philly

Senior Member
We have a 1-Phase 480V circuit that we need to supply a 70A breaker for. Should I supply a 2 pole or 3 pole breaker for this feeder circuit?

I know it should be a two pole breaker due to the single phase nature of the circuit, but in the event that sometime in the future this circuit was converted to a 3-phase service would it be a good idea to have a 3-pole breaker avaliable?

Or is putting a 3-pole breaker on a single phase service a code violation or not good practice?
 
What do you mean by "service"? Branch circuit? Ok if so, but may be wasteful.

But if you actually mean service when you say service, then 408.36(C) won't allow a 3-phase device to be installed in a single phase panel.
 
What do you mean by "service"? Branch circuit? Ok if so, but may be wasteful.

But if you actually mean service when you say service, then 408.36(C) won't allow a 3-phase device to be installed in a single phase panel.

This is actually a feeder branch circuit which will be feeding a 25kVA transformer.

I take it that a 3 pole breaker costs more than a 2-pole
 
Phil, if you're correct that a 3p breaker will eventually be installed, it could be better to install the 3p breaker now.

I guess the one ultimately paying the bill should be informed of the options and costs, and be allowed to decide.
 