1. 680.23(B)(2)(b) requires an INSULATED #8 conductor to be run in the conduit between the forming shell of a wet niche pool light to the junction box.
Question: What is the reasoning for the #8 to be installed within the conduit and why must it be insulated?
2. 680.24(B) permits a pool light transformer enclosure to connect directly to the conduit extending to the forming shell without a listed pool light j-box. Many, including the common Intermatic transformer, are marked as suitable for direct connection to the pool light.
Question: How do the typical transformer enclosures comply with 680.24(B)(1)(1)? A standard RNC terminal adaptor and locknut isn't considered a "hub" is it?
Question: What is the reasoning for the #8 to be installed within the conduit and why must it be insulated?
2. 680.24(B) permits a pool light transformer enclosure to connect directly to the conduit extending to the forming shell without a listed pool light j-box. Many, including the common Intermatic transformer, are marked as suitable for direct connection to the pool light.
Question: How do the typical transformer enclosures comply with 680.24(B)(1)(1)? A standard RNC terminal adaptor and locknut isn't considered a "hub" is it?