2 questions about different stuff

Status
Not open for further replies.
I have a service upgrade and the HO has a roll of nickel plated copper #4 bare wire for grounding purposes. Can i use nickel plated copper...what is the difference i cant find it in the nec 05, but i don't really know the classification.

AND... Can a dimmer be installed before a photocell on outdoor lights. How does a photocell work, because i put a dimmer before the PC and now if the lights are coming on extremely early. Will low voltage, because the dimmer, cause this? or is it just coincidence.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I would imagine that nickle plated copper is fine but I would not put a dimmer before a photocell. It will not work properly
 

480sparky

Senior Member
Location
Iowegia
The PC won't work on a dimmer because you're reducing the voltage to it.

The dimmer needs to be after (downstream from) the PC.
 
Status
Not open for further replies.