Question1:
220.82 says that the following conditions need to be met so that I can use the optional method for dwelling unit:
"This section applies to a dwelling
unit having the total connected load served by a single
120/240-volt or 208Y/120-volt set of 3-wire service or feeder
conductors with an ampacity of 100 or greater."
Most people's interpretation to this is that the voltage and ampacity of feeders conditions must be met to use optional method. However my interpretation is that only 1 of these conditions must be met because they don't use the word "and" they only use the word "or". See above text in red. Please clarify.
Question2:
Suppose I use optional method for a single dwelling unit and my demand load came out to be 100.6 amperes. Could I use a 100A breaker or will that not be code compliant and I would need the next size up? I mean it's only 0.6 Amperes over...
220.82 says that the following conditions need to be met so that I can use the optional method for dwelling unit:
"This section applies to a dwelling
unit having the total connected load served by a single
120/240-volt or 208Y/120-volt set of 3-wire service or feeder
conductors with an ampacity of 100 or greater."
Most people's interpretation to this is that the voltage and ampacity of feeders conditions must be met to use optional method. However my interpretation is that only 1 of these conditions must be met because they don't use the word "and" they only use the word "or". See above text in red. Please clarify.
Question2:
Suppose I use optional method for a single dwelling unit and my demand load came out to be 100.6 amperes. Could I use a 100A breaker or will that not be code compliant and I would need the next size up? I mean it's only 0.6 Amperes over...