The handle tie is an important element in this by the way. A classic example is the receptacle found under a sink, one for the garbage disposal, the other for the dishwasher. Both together is too much for one 20A circuit, so you run two sets of conductors and split the duplex receptacle, then tie it to a double pole CB. I had an apprentice do it once on a retrofit where he used 1/2 space breakers to squeeze them in, the AHJ bounced it because they could not have their handles tied together. The reason is, you don't want someone to plug a circuit finder into one receptacle to find the breaker to turn it off before working on it, only to discover when he opens the box that the other one is still hot! Tying the handles together means when you turn one off, you turn them both off before entering that box.