I have a job to installed 2 100 amp services take down old ones put up new. Here we are required to use only one ground rod. I will be using the same rod for the two services.
Now here's my question. Here we bond gas and water. Now can i use one continuous GEC from ground rod to each water and gas that enter each apartment separately? Basically one #6 to both apartments gas and water. If so what code section so I can tell inspector. He told me 2 separate #6, but why it is all bonded together, why not one gec?
Thanks for any help
Now here's my question. Here we bond gas and water. Now can i use one continuous GEC from ground rod to each water and gas that enter each apartment separately? Basically one #6 to both apartments gas and water. If so what code section so I can tell inspector. He told me 2 separate #6, but why it is all bonded together, why not one gec?
Thanks for any help