As Augie stated each building would require a GES using all electrodes present. It doesn't really matter if the two structures have water service from the same source. The 10' in contact with the earth is what really matters.
Here's a graphic from Mike:
http://www.mikeholt.com/onlinetraining/page_images
/1113918430_2.jpg
This is a great illustration. Notice how the second ground rod is jumped from the first. How do I do I convince my inspectors that doing this is code compliant? They want a continuous GEC from panel to first rod and on to the second rod.
This is a great illustration. Notice how the second ground rod is jumped from the first. How do I do I convince my inspectors that doing this is code compliant? They want a continuous GEC from panel to first rod and on to the second rod.
Show them the picture and tell them Rob said it was permissible
If continuous between buildings, that water pipe will be in parallel with the neutrals. Unavoidable, but it will probably carry some current.