2 sets of conductors (3-wire + ground), one is copper and the other is aluminum.

Status
Not open for further replies.
Yes, though only 1 is necessary for the 400A branch breaker it is fed from.

If say phase A has one aluminum conductor and one copper conductor it is a violation.

One the other hand if phase A is all copper and phase B is all aluminum that would be fine assuming correct sizing.
 