housemoney
Member
- Location
- Midwest
- Occupation
- Engr
Sanity check for me please: Contractor has (6) 600kcmil ungrounded conductors and (2) 2/0 grounded conductors per 5" conduitI calculated a minimum of 450kcmil grounded conductor with 12.5% rule? 2 -2/0's are not cutting it correct? I know you're required to run one per conduit, but is it permissible to run 2 smaller grounded conductors for a sum of 450kcmil?Thank you.