M mikeybmdb32 Member Dec 12, 2012 #1 Does code allow service conductors to change size along the run? For instance, can you come into a meter with 4/0 on the line side and leave the meter with 2/0 on the load side as long as 2/0 is large enough for the load?
Does code allow service conductors to change size along the run? For instance, can you come into a meter with 4/0 on the line side and leave the meter with 2/0 on the load side as long as 2/0 is large enough for the load?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Dec 12, 2012 #2 Always been NEC allowable as far as I know.
Smart $ Esteemed Member Location Ohio Dec 12, 2012 #3 I agree... as long as the service ocp is properly sized too.
david luchini Moderator Staff member Location Connecticut Occupation Engineer Dec 12, 2012 #4 I agree with Smart$ agreeing with Gus (Sorry, couldn't resist.)