Working on a project where 2 buildings are being combined as one occupancy. Side by side brick buildings.
The service with 2 main disconnect breakers is mounted at the exterior rear of building A and grounding of this service is attached to water line entering at the rear of this building A.
Now building B also has its own water service but enters completely opposite end of building which the owners at this point are not combining.
So the question is what is the code compliant way to bond this water service/copper line in building B with the water service in Building A.
A. Just bond the waterlines in both buildings together anywhere along there lengths.
B. Run bonding wire from within 5' of bldg A water entrance to building B waterline anywhere along its length.
C. Bond waterline to sub panel in building B anywhere along the length of waterline.
D. Bond waterline to subpanel in building B within 5' of water entry (as making it a 2nd grounding electrode), (? If the EGC feeding the subpanel can be used for the simultaneous purpose of GEC. Didn't 2014 allow this?)
E. Other I'm Open to suggestions/enlighten me.
Im a bit reserved thinking about if a potential fault occurred on the domestic water line (which has to go around a city block to serve both buildings) would a bonding wire be OK between buildings or could it become a fire hazard if it would need to carry fault current from one waterline to another by other services from other buildings. Have no idea if domestic waterlines underground are metallic around the city block.
The service with 2 main disconnect breakers is mounted at the exterior rear of building A and grounding of this service is attached to water line entering at the rear of this building A.
Now building B also has its own water service but enters completely opposite end of building which the owners at this point are not combining.
So the question is what is the code compliant way to bond this water service/copper line in building B with the water service in Building A.
A. Just bond the waterlines in both buildings together anywhere along there lengths.
B. Run bonding wire from within 5' of bldg A water entrance to building B waterline anywhere along its length.
C. Bond waterline to sub panel in building B anywhere along the length of waterline.
D. Bond waterline to subpanel in building B within 5' of water entry (as making it a 2nd grounding electrode), (? If the EGC feeding the subpanel can be used for the simultaneous purpose of GEC. Didn't 2014 allow this?)
E. Other I'm Open to suggestions/enlighten me.
Im a bit reserved thinking about if a potential fault occurred on the domestic water line (which has to go around a city block to serve both buildings) would a bonding wire be OK between buildings or could it become a fire hazard if it would need to carry fault current from one waterline to another by other services from other buildings. Have no idea if domestic waterlines underground are metallic around the city block.