For forty years I have preached that a breaker trips because it saw something on the load side it didn't like. I am wrong.
This is the third time that many houses all complained of multiple breakers tripping. All residential.
The POCO found one vacuum switch on a primary voltage capacitor bank, that when it closed, it malfunctioned and sounded like it was arcing.
The DFs didn't trip every time, and the affected customers were not on the same POCO phase or even the same circuit leaving the substation.
In the past, I only saw Square D DF breakers. QO and Homeline. This time there was an Eaton Cutler Hammer panel with DF breakers tripping.
All pretty crazy.
These POCO circuits have thousands of customers. They received five calls to complain.
These are the links for the last two I reported on this forum.
https://forums.mikeholt.com/threads...-in-blocks-of-four-in-several-houses.2580324/
https://forums.mikeholt.com/threads...f-breaker-tripping-and-strobing-leds.2586609/
This is the third time that many houses all complained of multiple breakers tripping. All residential.
The POCO found one vacuum switch on a primary voltage capacitor bank, that when it closed, it malfunctioned and sounded like it was arcing.
The DFs didn't trip every time, and the affected customers were not on the same POCO phase or even the same circuit leaving the substation.
In the past, I only saw Square D DF breakers. QO and Homeline. This time there was an Eaton Cutler Hammer panel with DF breakers tripping.
All pretty crazy.
These POCO circuits have thousands of customers. They received five calls to complain.
These are the links for the last two I reported on this forum.
https://forums.mikeholt.com/threads...-in-blocks-of-four-in-several-houses.2580324/
https://forums.mikeholt.com/threads...f-breaker-tripping-and-strobing-leds.2586609/