If you have a lighting circuit loading at 20amps on a #12thhn in a conduit can you just put a 25 amp breaker on it? Ampacity chart says #12thhn is good for 25amps in comduit
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Depending on what type of lighting circuit you might not even be allowed to load it 20 amps.
 

kwired

Electron manager
Location
NE Nebraska
If you have a lighting circuit loading at 20amps on a #12thhn in a conduit can you just put a 25 amp breaker on it? Ampacity chart says #12thhn is good for 25amps in comduit
Lighting is almost always a continuous load, so if you have an actual load of 20 amps you need a 24 amp circuit. This is also assuming you have lighting type that can be on more than a 20 amp circuit. Plus there is also the already mentioned 240.4(D)(5)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Lighting is almost always a continuous load, so if you have an actual load of 20 amps you need a 24 amp circuit. This is also assuming you have lighting type that can be on more than a 20 amp circuit. Plus there is also the already mentioned 240.4(D)(5)

Twenty five? :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Should have worded it better, I intentionally said 24 meaning conductor ampacity can't be less than 24, but yes 25 is next standard overcurrent device.

A 24 amp circuit is too small. :D {20*125% = 25}
 