376.56(A) Splices and Taps.
Splices and taps shall be permitted within a wireway, provided they are accessible. The conductors, including splices and taps, shall not fill the wireway to more than 75 percent of its area at that point.
I agree. With conductors of that size I would call it impossible to exceed the 75% fill even if you tried.And I'm willing to bet that the fill is nowhere as much as it appears.
The original install was 1953 lol. Not sure when additional circuits were added. Roughly 5000 sq feet original building and an additional 5000 added in around 1970Looks like it has survived the test of time so far and I can also say I seen very similar installs that lasted for 50 plus years as well.