I am trying to understand the logic of requiring us to connect to the rebar in a footing when 250.52(A)(3) gives us the option of "or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG." to qualify as a concrete encased electrode.
In other words; Could we not accept the 20' piece of copper layed in a footer along side of the rebar and not connect to the rebar? Why does a typically shorter piece have to be connected to the rebar via an approved clamp? Why do we have the impression that rebar MUST be connected to in the first place? Read 250.50 with out any prejudice or preconceived attitudes and see if you can see where we MUST connect to the rebar. Remember, rebar is ONE of the options listed in 250.52(A)(3) as an acceptable concrete encased electrode.
In other words; Could we not accept the 20' piece of copper layed in a footer along side of the rebar and not connect to the rebar? Why does a typically shorter piece have to be connected to the rebar via an approved clamp? Why do we have the impression that rebar MUST be connected to in the first place? Read 250.50 with out any prejudice or preconceived attitudes and see if you can see where we MUST connect to the rebar. Remember, rebar is ONE of the options listed in 250.52(A)(3) as an acceptable concrete encased electrode.