Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
I was wondering if this might by a typo because I was reading an exam prep question that was drawn right from this article (as indicated by "200.3" notation next to the question).
The question is True or False
"Premises wiring shall not be electrically connected to a supply system unless the supply system contains, for any grounded conductor of the interior system, a corresponding conductor that is ungrounded."
The code says this
200.3 Connection to Grounded System. Premises wiring
shall not be electrically connected to a supply system unless
the latter contains, for any grounded conductor of the interior
system, a corresponding conductor that is grounded. For the
purpose of this section, electrically connected shall mean connected
so as to be capable of carrying current, as distinguished
from connection through electromagnetic induction.
So what does it mean?
Any grounded conductor of the interior system requires a corresponding grounded conductor?
The question is True or False
"Premises wiring shall not be electrically connected to a supply system unless the supply system contains, for any grounded conductor of the interior system, a corresponding conductor that is ungrounded."
The code says this
200.3 Connection to Grounded System. Premises wiring
shall not be electrically connected to a supply system unless
the latter contains, for any grounded conductor of the interior
system, a corresponding conductor that is grounded. For the
purpose of this section, electrically connected shall mean connected
so as to be capable of carrying current, as distinguished
from connection through electromagnetic induction.
So what does it mean?
Any grounded conductor of the interior system requires a corresponding grounded conductor?