Just something I stumbled across when looking up something else.
200.3 Connection to Grounded System.
Premises wiring shall not be electrically connected to a supply system unless the latter contains, for any grounded conductor of the interior system, a corresponding conductor that is grounded. For the purpose of this section, electrically connected shall mean connected so as to be capable of carrying current, as distinguished from connection through electromagnetic induction.
From what I'm reading is this is saying that if we have a building that is supplyed by a ungrounded delta we are not allowed to use a transfomer to step off and feed for 120 volts?
This almost says that the service must supply the neutral if we are going to require a neutral in the building? And even sound's like even a zig-zag wouldn't be allowed.
What am I missing?
200.3 Connection to Grounded System.
Premises wiring shall not be electrically connected to a supply system unless the latter contains, for any grounded conductor of the interior system, a corresponding conductor that is grounded. For the purpose of this section, electrically connected shall mean connected so as to be capable of carrying current, as distinguished from connection through electromagnetic induction.