We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.
From the NEC 2002 Handbook. "Grounded conductors of premises wiring (other than separtely derived systems) must be connected to the supply system grounded conductor to ensure a common, continuous, grounded system."
I have discovered the reason for removing the section about auto-transformers. It was done due to the use was discontinued anyway. Standard two winding transformers replaced them.
200.3 Is to assure the utility MGN is connected to the X-O of the premises system, for the purpose of winding to winding faults.
I have been partly corrected in my previous explanation of my interpretation of 200.3.
A grounded premises wiring system can not be electrically connected to an ungrounded supply, except by magnetic coupling.
Electrically connected shall mean capable of carrying current.