(NEC 2014) 200.4(B) says neutrals shall be identified or grouped to correspond with ungrounded conductors by wire markers, cable ties, ...
Does this mean I can just put matching numbers on the neutrals and hots and they don't have to be physically tied together?
Inspector said: separate neutral and pair up to branch circuit with wire ties label as individual circuit in new panel as per NEC article 200.4 B
which seems to indicate he wants them tied together.
(Before you start pointing to the exceptions, I extended the wires from the old panel into a new one so no overall jacket.)
Does this mean I can just put matching numbers on the neutrals and hots and they don't have to be physically tied together?
Inspector said: separate neutral and pair up to branch circuit with wire ties label as individual circuit in new panel as per NEC article 200.4 B
which seems to indicate he wants them tied together.
(Before you start pointing to the exceptions, I extended the wires from the old panel into a new one so no overall jacket.)