I understand 250.119 (A) about not being allowed to phase tape 6 AWG and smaller for the grounding conductor. What about 200.6? Can we phase tape the grounded conductor when using 6 AWG or smaller other than green wire?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
The Iceman said:
I understand 250.119 (A) about not being allowed to phase tape 6 AWG and smaller for the grounding conductor. What about 200.6? Can we phase tape the grounded conductor when using 6 AWG or smaller other than green wire?

No. 200.6(B) Larger than 6 AWG
 