Minuteman

Senior Member
Starting with the basics in my class. Going over 200.6 and I got to thinking about URD having a yellow stripe on the grounded conductor. How is a yellow stripe code compliant? :-?
 

hillbilly

Senior Member
Starting with the basics in my class. Going over 200.6 and I got to thinking about URD having a yellow stripe on the grounded conductor. How is a yellow stripe code compliant? :-?


That's a good question.:)

My guess, and that's what it is, a guess, is that since URD is normally used for service cable, and since most service cable is "owned" by the POCO (conductors before the meter), the NEC rules don't apply.

steve
 

Smart $

Esteemed Member
Location
Ohio
Starting with the basics in my class. Going over 200.6 and I got to thinking about URD having a yellow stripe on the grounded conductor. How is a yellow stripe code compliant? :-?
URD isn't per se a cable type. It's an acronym for Underground Residential Distribution and encompasses several cable types. Typically this will be a Type USE multiconductor cable for a service or service entrance conductors. Color and tracer markings of most cable conductors are outside the purview and control of the NEC, and thus may require proper [re]identification or documentation to be NEC compliant.
 

Minuteman

Senior Member
URD isn't per se a cable type. It's an acronym for Underground Residential Distribution and encompasses several cable types. Typically this will be a Type USE multiconductor cable for a service or service entrance conductors. Color and tracer markings of most cable conductors are outside the purview and control of the NEC, and thus may require proper [re]identification or documentation to be NEC compliant.

So, when we install it as a feeder/branch circuit we need to mark the grounded conductor properly. Thanks!
 