Starting with the basics in my class. Going over 200.6 and I got to thinking about URD having a yellow stripe on the grounded conductor. How is a yellow stripe code compliant? :-?
 
Starting with the basics in my class. Going over 200.6 and I got to thinking about URD having a yellow stripe on the grounded conductor. How is a yellow stripe code compliant? :-?


That's a good question.:)

My guess, and that's what it is, a guess, is that since URD is normally used for service cable, and since most service cable is "owned" by the POCO (conductors before the meter), the NEC rules don't apply.

steve
 
Starting with the basics in my class. Going over 200.6 and I got to thinking about URD having a yellow stripe on the grounded conductor. How is a yellow stripe code compliant? :-?
URD isn't per se a cable type. It's an acronym for Underground Residential Distribution and encompasses several cable types. Typically this will be a Type USE multiconductor cable for a service or service entrance conductors. Color and tracer markings of most cable conductors are outside the purview and control of the NEC, and thus may require proper [re]identification or documentation to be NEC compliant.
 
URD isn't per se a cable type. It's an acronym for Underground Residential Distribution and encompasses several cable types. Typically this will be a Type USE multiconductor cable for a service or service entrance conductors. Color and tracer markings of most cable conductors are outside the purview and control of the NEC, and thus may require proper [re]identification or documentation to be NEC compliant.

So, when we install it as a feeder/branch circuit we need to mark the grounded conductor properly. Thanks!
 