We have two systems entering the same enclosure in multiple places
site wide: specifically 208/120V and 480/277V.
The inspectors have stated; according to 200.6, we needed to add labeling on each enclosure stating the voltages and phase/ neutral conductors color coding, ie white and gray respectively.
Does the labeling necessarily have to be the permanent nameplate type with adhesive backing or attaching screws? Or can it be a simple sheet of laminated paper posted on the enclosure or nearby?