What does 2014 code section 200.7e cover?
Inspector listed it as switches
Not sure what he means
200.7 covers identification of the neutral/ grounded conductor
There is a dearth of details here, but I'm going to take a stab at it- the inspector got somebody for not properly id'g a switch leg/loop?
this is residential new home.
Romex wiring
Must be the 3 way switch legs
He also listed 110.3b Smokes near fans
Does he mean smoke detectors from ceiling fans?
Whats the clearance required?
As for the smokes, he likely means that the installation violated the instructions/listing (110.3 B) from manufacturer of the smokes- need to have 3 feet from smokes to CF blade tip.
And when you move them, make sure they arent then within 3' of an air return, or (I think) 10' of a shower, and... read the manual. It will have all the specs in it.
And when you move them, make sure they arent then within 3' of an air return, or (I think) 10' of a shower, and... read the manual. It will have all the specs in it.
What does 2014 code section 200.7e cover?
Inspector listed it as switches
Not sure what he means
In addition to the manufacturer's installation instructions....
NFPA 72, sec 11.8.3.5 (5) Smoke alarms shall not be installed within a 36 in. horizontal path from a door to a bathroom containing a shower or tub.
(6) ......shall not be installed within a 36 in. horizontal path from the supply registers of a forced air heating or cooling system and shall be
installed outside of the direct airflow from those registers.
(7) ......shall not be installed within a 36 in. horizontal path from the tip of the blade of a ceiling-suspended (paddle) fan.
If your jurisdiction has not adopted NFPA 72, then, nevermind![]()
Thank guys. The bedrooms are small maybe 10 x 10
Does putting SA on the wall add any distance?