Would someone please reference any or all related Code articles that would justify the installation of a 200A subpanel (distribution only) downline from a 100A meter/main switch service as OK?
We're at the limit space-wise, so I as many of my peers do and suggest doing, install a 20/40 sized panel, typically a 200A sub with distribution only, to accomodate all the breakers.
The inspector I queried on this had me a bit confused and made me wonder if I was missing something. As far as I can tell, if the demand on the panel is less than the rating of the main switch, then the downline panel could be any size so long as the feeders are protected with a overcurrent device that is properly sized for the wire.
Chime in, please.
Thanks!
Bob
We're at the limit space-wise, so I as many of my peers do and suggest doing, install a 20/40 sized panel, typically a 200A sub with distribution only, to accomodate all the breakers.
The inspector I queried on this had me a bit confused and made me wonder if I was missing something. As far as I can tell, if the demand on the panel is less than the rating of the main switch, then the downline panel could be any size so long as the feeders are protected with a overcurrent device that is properly sized for the wire.