200 amp 120-240v transfer switch
Mr. M
CT
Upon a recent call, I was asked if the installation of a transfer switch in this residential location
was installed per code. I noticed that the load side SE (4/0 Al.) cable from the meter to the 200
amp panel had been removed and replaced with a longer piece, so it would reach the transfer
switch located adjacent to the panel. I didn't see any labeling that it was rated for service
disconnect. The load side from the transfer switch re-supplied the main panel via a 2" piece of
pvc, with 4/0 Al. installed within.
My question is does the existing 200 amp. panel still remain as the main service disconnect?,
and if not would the main bonding jumper have to be removed and neutrals and grounding
conductors be isolated.
If the electrical panel served as the service disconnecting means then the transfer switch would have to be listed as suitable as service equipment because it is now located upstream from the panel. The manin bonding jumper would have to be located in the transfer switch.
Chris
Transfer sw.
Transfer sw.
Chris
Would the neutrals and equipment grounds has to be isolated also?