200 amp 240 v at the breaker panel

Status
Not open for further replies.
L

Lxnxjxhx

Guest
Let's say with zero load on this service you have exactly 240 volts.
Does this mean that with a full load, 200 amps in this case, you will see a 3% drop in voltage?

I'm getting at the Thevenin equivalent impedance at the breaker panel; I know it's about 1/4 ohm at the outlets.

Also, if there is corrosion upstream, this impedance should increase and you have lights dimming depending on the load.
 
langjahr@comcast.net said:
Does this mean that with a full load, 200 amps in this case, you will see a 3% drop in voltage?
Nope. There is no relationship (at least not one that can be used in a calculation) between the panel's current rating and its internal resistance. Besides, I don't think it reasonable to expect a 3% voltage drop within the panel itself. It is built out of large copper bars, not small wires.
 
Then does anyone know of specs to pass or fail an existing service?

There does seem to be spec limits on the current in neutrals and ground resistance, and I think breakers are not supposed to have over 30 mV across the closed contacts at full load current.
 