200 Amp 3 pole Siemens shunt trip beaker

Merry Christmas
Location
New York
Occupation
Electric al contractor
hi, I have job in medical clinic to contact shunt trip breaker with disconnect switch.
I don’t have any diagram as it’s old breaker. Qj23b200.
It has 4 wires 1 white and 3 black. Blacks are marked as A, S and T.
I am attaching photos for the breaker and switch.
Thank you
 

Attachments

  • 9aba8247-bc20-41ed-a378-5df381be4bbe.jpeg
    9aba8247-bc20-41ed-a378-5df381be4bbe.jpeg
    772.4 KB · Views: 10
  • e590517a-5b56-4a3b-9955-84eaac6266c1.jpeg
    e590517a-5b56-4a3b-9955-84eaac6266c1.jpeg
    961.5 KB · Views: 10
  • 783092791.jpeg
    783092791.jpeg
    616.3 KB · Views: 9
  • 783092778.jpeg
    783092778.jpeg
    546.1 KB · Views: 9
A and white are the aux contacts, S and T are the trip coil.

I suggest wiring the switch in series with the coil. For example:

Connect A to S (or T), connect the white to the neutral bar, and connect T (or S) to the incoming tripping voltage source.
 
I am attaching the photos
A & c wire nut together, c (white) into neutral.
T to black ((14/2) coming from switch,
14/2 white to line
 

Attachments

  • IMG_1624.jpeg
    IMG_1624.jpeg
    1.2 MB · Views: 5
  • IMG_1623.jpeg
    IMG_1623.jpeg
    979.1 KB · Views: 5
  • IMG_1622.jpeg
    IMG_1622.jpeg
    1.4 MB · Views: 5
That should be A and S connected together, not A and C, I think.

Power to white of 14-2 to the tripping switch, returning on black to T to coil, S from coil to A, white to neutral in panel.

120v will trip the coil, then the aux. contacts will instantly open, so the trip coil will not overheat from constant power.
 