alyoshak24
Member
- Location
- Chicago
- Occupation
- Electrician
BACKGROUND - Installing Grounding Electrode System for a 2 story 2 tenant house in Chicago each floor having a corresponding meter. After Driving 2 ground rods 8 ft apart from each other and running my green #8 to the meter enclosure, i attempted to terminate into the grounding lug (which is usually below or adjacent to the grounded lug of meter box and usually smaller than the grounded lug) but this meter enclosure, which is older ring style, does not have that adjacent grounding lug. This is getting expected next week and need to reconcile this issue; my question to the Masters/Experts nationwide is:
**** Can you please provide NEC excerpts/sources sited or supplemental YouTube vids or pics of your guys work how you got a similar situation to work out. ****
THANK YOU MAESTRO'S
- Can i terminate the GEC to the load side neutral lug of either meter can ? if not then ~
- Can I terminate the GEC to the grounding bushing on either of the 1/2 or 3/4 EMT grounding bushings and leave it at that since the Neutral lug is bonded to the meter enclosure? if not then ~
- Since it is mounted on brick, drilling and tapping is out of the question, is there a GEC lug kit for this MURRAY model double ring meter can (Retrofit code compliant GEC Kits) ? if there arent then ~
- what do i do in this situation of 1 - 3 are not an option or against code ?
**** Can you please provide NEC excerpts/sources sited or supplemental YouTube vids or pics of your guys work how you got a similar situation to work out. ****
THANK YOU MAESTRO'S