Tim11
Member
- Location
- Oakland, Michigan.
- Occupation
- Journeyman Electrician
Hi everyone looking for a help and advice. This is probably a pretty common scenario in a dwelling but I work commercial and Industrial so wanted to run it by those of you who who would more familiar just in case I'm missing anything.
A friend of my family purchased a 22kw standby generac kit which came with a 200 amp service rated ATS. Anyways, I am curious if there any issues or violations with utilizing the 200 amp ats without having to upgrade his exsisting 150 amp panel?
His meter can and lateral are both rated for 200 amps. So as long as I upgraded his service entrance conductors to the utility side of the ATS with a 4/0 AL. Then sub fed his 150 amp main breaker panel with 4/0 AL or a 2/0 Cu plus a #6 equipment ground I don't think there would be any issues besides changing his cold water bond to a #4 cu.
Would appreciate any input and or advice...
A friend of my family purchased a 22kw standby generac kit which came with a 200 amp service rated ATS. Anyways, I am curious if there any issues or violations with utilizing the 200 amp ats without having to upgrade his exsisting 150 amp panel?
His meter can and lateral are both rated for 200 amps. So as long as I upgraded his service entrance conductors to the utility side of the ATS with a 4/0 AL. Then sub fed his 150 amp main breaker panel with 4/0 AL or a 2/0 Cu plus a #6 equipment ground I don't think there would be any issues besides changing his cold water bond to a #4 cu.