Hi everyone; I haven't posted before, hope this is the correct spot. Anyway, I was wondering if you could help me out with something that could potentially be obvious to everyone except me.
Say we are eliminating an old 60a service - fuses to breakers. We are re-doing everything, moving the meter to outside from inside etc.. Calculated load on the existing home is much less than 100 amps. Customer opts to upgrade to a 100 amp service instead of a 200 amp service because the price difference is significant due to what is needed for the mast and feeder piping etc.
So, will NEC allow me to use a 200 amp MCB (with the 8 space panel and feed thru lugs) as the emergency shut off on the exterior and jump off the feed thru lugs with my 4 AWG so long as I land immediately inside the house into a 100 MCB load center? Seems legal per 240 outside tap rule, but I also feel like I am missing something obvious here.... P.S. I'm aware this isn't ideal, a 100 amp version of this meter main combo is not available to me in this scenario.. Thanks in advance
Say we are eliminating an old 60a service - fuses to breakers. We are re-doing everything, moving the meter to outside from inside etc.. Calculated load on the existing home is much less than 100 amps. Customer opts to upgrade to a 100 amp service instead of a 200 amp service because the price difference is significant due to what is needed for the mast and feeder piping etc.
So, will NEC allow me to use a 200 amp MCB (with the 8 space panel and feed thru lugs) as the emergency shut off on the exterior and jump off the feed thru lugs with my 4 AWG so long as I land immediately inside the house into a 100 MCB load center? Seems legal per 240 outside tap rule, but I also feel like I am missing something obvious here.... P.S. I'm aware this isn't ideal, a 100 amp version of this meter main combo is not available to me in this scenario.. Thanks in advance