milemaker13
Senior Member
- Location
- Suburbs of Chicago
200 amp, 480 volt, 3 phase breaker feeding subpanel. The sub panel has two, 100 amp breakers feeding large dust collectors.
Maintenance guys say they can run either machine separately with no problem. But if they run both together, the 200 amp breaker feeding the panel will trip. Some times it takes an hour, sometimes it's after lunch.
Each machine is drawing 40- 50 amps, for a total of about 90. ( the motors on these dust collectors should be drawing about 90 amps each, so i assume they are running basically no- load). These machines have been running for several years now ( not newly installed).
I put 3 meters on the incoming power, and never got anything more than about 90 amps total when it tripped the 200 amp breaker.
I'm going to check connections and such when i can shut them both down but I'm wondering if anyone has any ideas. Thanks.