We Installed a new trane RTU (hvac) that had a max amp rating of 150 amps.
We used the original conductors & breaker in the building and used a 200amp disconnect with 150 amp fuses to lower the amperage.
The new building inspector for the town said we have to change the breaker in the building to 150amp breaker unless we could show her something from the NEC book that allows you to use fuses to lower amperage.
It seems like common sense to me.
But I went digging into the 2020 NEC book anyway and,
I cannot find anything & I'm running out of time, she gave us till EOD to come up with something.
Any idea
We used the original conductors & breaker in the building and used a 200amp disconnect with 150 amp fuses to lower the amperage.
The new building inspector for the town said we have to change the breaker in the building to 150amp breaker unless we could show her something from the NEC book that allows you to use fuses to lower amperage.
It seems like common sense to me.
But I went digging into the 2020 NEC book anyway and,
I cannot find anything & I'm running out of time, she gave us till EOD to come up with something.
Any idea