200 Amp Disconnect Switch

Status
Not open for further replies.

tommygary

Member
Location
New York
Can I cross my line and load wires in a 200 amp disconnect switch? The line comes into the switch in the bottom and the load enters the top. In order to terminate in the switch, the conductors will cross. Is this a violation or is this acceptable?
 
Can I cross my line and load wires in a 200 amp disconnect switch? The line comes into the switch in the bottom and the load enters the top. In order to terminate in the switch, the conductors will cross. Is this a violation or is this acceptable?
In general, the exposed blades of a disconnect switch are expected to be de-energized when switch is open.

Because the "blades" of a circuit breaker are not exposed, this restriction does not usually exist with molded case switches.
 
They can cross.

The only relevant code article I can think of is the one mentioning wire fill. 312.8 maybe?
 
Last edited:
They can cross.

The only relevant code article I can think of is the one mentioning wire fill. 312.8 maybe?

My bad.

I did not notice the OP simply wanted to cross the wires.
The only code issue might be the physical room in the cabinet.
 