200 amp main breaker---100 amp service conductors

Status
Not open for further replies.
Art 240 is your reference as well as 230.90. If you have no overcurrent protection ahead of your #2s the 240.4 would prohibit the install& 230.90 would require OCP
If your #2s have properly sized overcurrent protection ahead of them (at the meter) then the interior panel breaker could be any size. It's just a disconnect.
 