I have a 200 amp three phase fused disconnect switch only and I would like too know if I can use a main lug panel as my primary
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

If you mean feed the ML panel from the fuses, yes, as long as you're in the same structure.
 

L4nd0n40

Member
Location
Louisiana
Occupation
Apprentice Electrician
Also, Mr. Larry, I do have a question I’m still learning can I run single phase off of a three phase service
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I think we need more information. Is this a real situation or something for your education?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
And if so, how do I achieve that I would assume just running it off of one leg, right?

Also, Mr. Larry, I do have a question I’m still learning can I run single phase off of a three phase service
If you have 208Y/120, then you have three single-phase 120v line-to-neutral sources, and/or three single-phase 208v line-to-line sources.

This is pretty basic stuff.
 

L4nd0n40

Member
Location
Louisiana
Occupation
Apprentice Electrician
If you have 208Y/120, then you have three single-phase 120v line-to-neutral sources, and/or three single-phase 208v line-to-line sources.

This is pretty basic stuff.
I am an apprentice and I am just doing my research too understand and make sure the job is done properly! I appreciate your help very much
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I am an apprentice and I am just doing my research too understand and make sure the job is done properly! I appreciate your help very much
Thank you for telling us where you are coming from. Do you have supervision on site?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It is common to take a single phase feeder, which would consist of two hots and the neutral, off a three phase system.
Yes. It depends on the electrical needs of the devices you're looking to supply power to.