This is a ranch property setup, all separate buildings. Standard 3 bed 2.5 bath house with electric appliances and propane range. Occasional welder use off of a sub panel. Future garage sub panel will be big enough for electric car charger if needed in future. 200 amp service should be plenty for the property. All original wiring/panels (SP-1 & SP-2) from early 2000's unknown installer, not to current code with grounding and wire size. I want these electrical additions done per code even though it is outside any jurisdictions.
See pictures below for more info.
Questions:
Q1 - Confirming all panels after new (MP-1) are to be considered sub panels and will need 4 wires to each sub panel (2 hot, 1 neutral, 1 ground) along with ground bars added and sub panels unbonded.
Q2 - What size ground would you use for the sub panels, 2 AWG AL min or just go with 2/0 AL?
Q3 - Do I connect existing SP-1 T-pole ground rod and SP-2 ufer ground rod to ground bars I am adding in these sub panels, and then the ground bars will also be connected to 4th wire 2 AWG ground going back to MP-1?
Q4 - From new (MP-1) 200 amp main panel to (SP-1) 200 amp sub panel on existing pole and 200 amp house sub panel (SP-2) I intend on using QTY (3) 250 MCM AL and QTY (1) 2 AWG AL ground for the wiring. 4/0 AL is undersized for 200 amps @75 degree C ampacity on the equipment. Wanting to confirm wire order in picture before ordering.
See pictures below for more info.
Questions:
Q1 - Confirming all panels after new (MP-1) are to be considered sub panels and will need 4 wires to each sub panel (2 hot, 1 neutral, 1 ground) along with ground bars added and sub panels unbonded.
Q2 - What size ground would you use for the sub panels, 2 AWG AL min or just go with 2/0 AL?
Q3 - Do I connect existing SP-1 T-pole ground rod and SP-2 ufer ground rod to ground bars I am adding in these sub panels, and then the ground bars will also be connected to 4th wire 2 AWG ground going back to MP-1?
Q4 - From new (MP-1) 200 amp main panel to (SP-1) 200 amp sub panel on existing pole and 200 amp house sub panel (SP-2) I intend on using QTY (3) 250 MCM AL and QTY (1) 2 AWG AL ground for the wiring. 4/0 AL is undersized for 200 amps @75 degree C ampacity on the equipment. Wanting to confirm wire order in picture before ordering.